Intumescent strips.

Intumescent strips.

Postby HeadlessHarry » March 25th, 2009, 10:33 am

Does intumescent strip fitting to existing doors need to be certified or done by a particular person?

H
HeadlessHarry
Forum Newbie
 
Posts: 4
Joined: October 23rd, 2008, 8:39 am

Re: Intumescent strips.

Postby FlameContain » March 25th, 2009, 11:24 pm

I would reccomend that the fitting of the intumescent seals for existing doors should be carried out by a competent person although I don't believe that a formal qualification exists for such a person, this type of work is often carried out by carpenters. It is important to ensure that the seals have been successfully tested to BS 476 Part 22 and that they are fitted correctly after all it is a life safety requirement for fire doors to have intumescent strip to seal the gap around the door. A 30 minute fire door can be breached by fire within minutes if the gap is not sealed. As for certification of the door that depends on why you are fitting the intumescent - routine maintenance, refurbishment, upgrading the door etc. let me know why you are carrying out the work, what type of building it is and I should be able to tell you whether you need a certificate.

If you are fitting intumescent strips to an existing door there are a number of factors you should take into account the first is to determine the fire rating of the door, a timber door is usually rated at 30 or 60 minutes. A simple method of determining the rating where no label is visible on the door is to measure the door thickness, 44mm for FD30 and 55mm for a 60 minute door. You should fit seals with a fire integrity rating to suit the door i.e a 30 minute or 60 minute strip. A 30 minute strip will usually measure 10 x 4mm or 15 x 4mm and for a 1 hour door the strip will normally measure 20 x 4mm. It is not uncommon for two half hour strips to be installed on a one hour door.

The next step is to determine whether or not the door requires protection against the passage of smoke as well as fire, if smoke sealing is required then you should fit an intumescent strip with a smoke seal, this takes the form of a brush or rubber type fin built into the intumescent strip. Once a smoke seal has been fitted you should ensure that if the door is self closing i.e has a door closer fitted, that the door closes fully into the frame, often you will find that the door will not pass the smoke seal and fully latch, you should adjust the door closer accordingly to overcome the smoke seal.

The seals can be fitted into the door or frame and should be installed down each edge and across the top. It should also be noted that to fully comply with the requirements of BS 476 any ironmongery on the door should also be protected. This matter is often over looked. Hinges should have intumescent hinge pads or gasket fitted between each leaf of the hinge and the door and frame. Any lock case fitted to the door should also be wrapped in an intumescent gasket.

I hope I have answered your question, feel free to get back in touch if you need any clarification.
FlameContain
Forum Newbie
 
Posts: 3
Joined: March 17th, 2009, 9:48 am

Re: Intumescent strips.

Postby HeadlessHarry » March 30th, 2009, 7:36 am

No,no!

You've been very comprehensive in your answer.


Thank you very much!
HeadlessHarry
Forum Newbie
 
Posts: 4
Joined: October 23rd, 2008, 8:39 am

Re: Intumescent strips.

Postby bobby » July 1st, 2010, 12:36 pm

I completely agree with Headless, i have just recently upgraded some flats i let out and was pleased that i'd read through the Fire Safety Order as it proved invaluable in ensuring the flats were correctly protected. You can only go so far with extinguishers and sprinklers and in occasions such as mine it just wasnt possible to fit a sprinkler system. By using the correct intumescent smoke seals, fitting hinge and lock protection i upgraded my fire doors to the correct standard which complied with the independent risk assessment. The outlay isnt expensive and there are some great web sites that have passive protection available.

Bob